In preparation for creating our company families library, I compiled a list of all the family parameters included Out of the Box with Revit MEP 2016.
My goal is to avoid creating custom families, and parameters whenever possible - especially where there is already a place for the information. Autodesk did not have any documentation (I asked them), so I used the Family Templates and recorded the parameters in each. I plan to distribute to each discipline (M,E,P,FP,T) to familiarize them with Revit's organization, and also to get input on BIM parameters that we will need to add for scheduling and families.
This is what I have found:
Note: Based on Revit MEP 2016 Family Templates.Note: Parameters listed below are Text unless noted otherwise.Note: “Type” parameters cannot vary by instance. “Instance” Parameters can vary for each individual instance placed, and are usually followed by (default). Parameters listed below are “Type” Parameters unless noted “-per instance.”
All Revit MEP Families contain the following basic parameters, grouped under “Identity Data.”
My goal is to avoid creating custom families, and parameters whenever possible - especially where there is already a place for the information. Autodesk did not have any documentation (I asked them), so I used the Family Templates and recorded the parameters in each. I plan to distribute to each discipline (M,E,P,FP,T) to familiarize them with Revit's organization, and also to get input on BIM parameters that we will need to add for scheduling and families.
This is what I have found:
Note: Based on Revit MEP 2016 Family Templates.Note: Parameters listed below are Text unless noted otherwise.Note: “Type” parameters cannot vary by instance. “Instance” Parameters can vary for each individual instance placed, and are usually followed by (default). Parameters listed below are “Type” Parameters unless noted “-per instance.”
All Revit MEP Families contain the following basic parameters, grouped under “Identity Data.”
- Type Image (Image)
- Keynote (select from associated csv keynote file)
- Model
- Manufacturer
- Type Comments
- URL (URL)
- Description
- Assembly code (select from Uniformat Selection Box)
- Cost
There are also specific parameters included with some MEP Family Categories. Below is a list of MEP Family Categories, and their specific parameters.
Air Terminals (Registers, Grilles, Diffusers):
Air Terminals (Registers, Grilles, Diffusers):
- Max Flow (Air Flow)
- Min Flow (Air Flow)
- Cable Tray Fittings:
- Use Annotation Scale (Y/N - per instance)
- Communication Devices:
- No specific parameters for Communication Devices.
- Conduit Fittings:
- Use Annotation Scale (Y/N - per instance)
- Bend Radius (Conduit Size - per instance)
- Possible to add "Connector" parameters - see below.
Data Devices:
- No specific parameters for Data Devices.
- Possible to add "Connector" parameters - see below.
Duct Accessories (dampers, filters, smoke detectors):
- Use Annotation Scale (Y/N - per instance)
- Possible to add "Connector" parameters - see below.
Duct Fittings:
- Use Annotation Scale (Y/N - per instance)
- Possible to add "Connector" parameters - see below.
Electrical Equipment (Panels, Switchgear):
- Voltage
- Wattage
- Enclosure (per instance)
- Mounting (per instance)
- Panel Name (per instance)
- Neutral Rating (demand factor)
- Neutral Bus (Y/N)
- Ground Bus (Y/N)
- Bussing
- SubFeed Lugs (Y/N)
- MCB Rating (Current)
- Mains Type
- Feed (per instance)
- Circuit Naming (Panel Name/Prefixed/Standard/By Phase - per instance)
- Circuit Prefix Separator (per instance)
- Circuit Prefix (per instance)
- Modifications (per instance)
- Mains (Current – per instance)
- Short Circuit Rating (per instance)
- Max #1 Pole Breakers (Integer - per instance)
- Distribution System (Linked to Systems Tool - per instance)
- Possible to add "Connector" parameters - see below.
Electrical Fixtures (Receptacles, Junction boxes):
- No specific parameters for Electrical Fixtures.
- Possible to add "Connector" parameters - see below.
Fire Alarm Devices (Smoke Detectors, Pull Stations, Annunciators):
- No specific parameters for Fire Alarm Devices.
- Possible to add "Connector" parameters - see below.
Generic Models:
- No specific parameters for Generic Models.
Lighting Devices (Switches, Controls, Sensors):
- No specific parameters for Lighting Devices.
- Possible to add "Connector" parameters - see below.
Lighting Fixtures (Ceiling, Wall, Recessed Lights):
- Lamp
- Wattage Comments
- Calculate coefficient of Utilization (Y/N – per Instance)
- Coefficient of Utilization (Number - per instance)
- Apparent Load (Apparent Power)
- Possible to add "Connector" parameters - see below.
Mechanical Equipment (Boilers, Furnaces, Fans):
- No specific parameters for Mechanical Equipment.
- Possible to add "Connector" parameters - see below.
Nurse Call Devices:
- No specific parameters for Nurse Call Devices.
- Possible to add "Connector" parameters - see below.
Pipe Accessories (Connectors, Valves, and In-Line Water Heaters):
- Use Annotation Scale (Y/N – per instance)
- Loss Method (Not Defined, K Coefficent, or K Coefficient from Table)
- K Coefficient Table (linked to Project Settings)
- Possible to add "Connector" parameters - see below.
Pipe Fittings:
- Use Annotation Scale (Y/N – per instance)
- Loss Method (Not Defined, K Coefficent, or K Coefficient from Table)
- K Coefficient Table (linked to Project Settings)
- K Coefficient (Number)
- IsCustom (Y/N – per instance)
- Possible to add "Connector" parameters - see below.
Plumbing Fixtures (Sinks, Water Closets, Tubs, Drains):
- Vent Connection (Y/N)
- Waste Connection (Y/N)
- CW Connection (Y/N)
- HW Connection (Y/N)
- CWFU (Fixture Units)
- HWFU (Fixture Units)
- WFU (Fixture Units)
- V
Security Devices:
- No specific parameters for Security Devices.
- Possible to add "Connector" parameters - see below.
Sprinklers:
- Diameter (Pipe Size)
- Orifice Size (Pipe Size)
- Temperature Rating (Temperature)
- K-Factor (Number)
- Pressure Class (Standard or High Pressure)
- Orifice (Standard, Small, or Extra Large)
- Coverage (Standard or Extended)
- Response (Standard or Quick)
- Possible to add "Connector" parameters - see below.
Telephone Devices:
- No specific parameters for Telephone Devices
- Possible to add "Connector" parameters - see below.
***************[Updated]**************
"Connectors" - can be nested into families above to allow Revit MEP Systems Calculations
Here is a list of their parameters. Also refer to Autodesk Help – Connector Properties
Electrical Connector:
System Type: Data, Telephone, Security, Fire Alarm, Nurse Call, Controls, Communication
- [*=1]Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
[*=1]Connector Description
System Type: Power Balanced
- [*=1]Number of Poles (Integer)
[*=1]Power Factor State (Lagging/Leading)
[*=1]Load Classification (HVAC, Lighting, Motor, Power, Other)
[*=1]Load Sub-Classification Motor (Y/N)
[*=1]Voltage (#.##V)
[*=1]Apparent Load (#.##VA)
[*=1]Power Factor (Number 1.0)
[*=1]Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
[*=1]Connector Description (text)
System Type: Power Unbalanced
- [*=1]Same as Power Balanced except Apparent Load broken into phases
[*=1]Apparent Load Phase 1 (#.##VA)
[*=1]Apparent Load Phase 2 (#.##VA)
[*=1]Apparent Load Phase 3 (#.##VA)
Duct Connector:
- Flow Factor (Number)
- Loss Coefficient (Number)
- Flow Configuration (Calculated,Preset,System)
- Flow Direction (In, Out, Bi-directional)
- System Classification (Supply Air, Return Air, Exhaust Air, Other, Fitting-specify angle, Global)
- Loss Method (Not Defined, Coefficient, Specific Loss)
- Pressure Drop (#.## in-wg)
- Flow (#.## CFM)
- Shape (Round, Rectangular, Oval)
- Height
- Width
- Diameter
- Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
- Connector Description (Text)
Pipe Connector:
- K Coefficient (Number)
- Flow Factor (Number)
- Flow Configuration (Calculated, Preset, System)
- Flow Direction (In, Out, Bi-directional)
- Loss Method (Not Defined, Coefficient, Specific Loss)
- Allow Slope Adjustments (Y/N)
- System Classification (Hydronic Supply, Hydronic Return, Sanitary, Vent, Domestic Hot Water, Domestic Cold Water, Other, Fire Protection Wet, Fire Protection Dry, Fire Protection Pre-Action, Fire Protection Other, Fitting-specify angle, Global)
- Flow (#.## GPM)
- Pressure Drop (#.## in-wg)
- Diameter
- Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
- Connector Description (Text)
Cable Tray Connector:
- Angle
- Height
- Width
- Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
- Connector Description (Text)
Conduit Connector:
- Angle
- Height
- Width
- Utility (Y/N) – will export connector as a site utility to AutoDesk Exchange File
- Connector Description (Text)
Comment