    Plumbing family - Fixture Units

    Someone in my company created plumbing fixture families, but they don't translate the fixture units to the piping. I added them as an instance parameter, but I still can't get them to add up along the piping. Any suggestions as to why they wouldn't?

  2. #2
    Forum Addict josephpeel's Avatar
    Join Date
    May 3, 2012
    Posts
    1,401
    Current Local Time
    06:08 AM
    The plumbing fixture needs to have a connector with the "Fixture Units" type (Instead of flow).
    Then link your instance/type parameter to the fixture units in the connector.

    The piping system also needs to be set to fixture units and then it should work.

Similar Threads

  1. Section cut goes through Non-Cuttable family (plumbing fixture). What should I do?
    By ryntau in forum Architecture and General Revit Questions
    Replies: 3
    Last Post: March 24th, 2016, 02:14 PM
  2. Plumbing Fixture Family Anomaly in Arch Model
    By Charles Karl in forum Architecture and General Revit Questions
    Replies: 5
    Last Post: July 2nd, 2015, 03:23 PM
  3. Plumbing Fixture units
    By nick_h in forum MEP - General
    Replies: 6
    Last Post: October 17th, 2014, 11:42 AM
  4. Having difficulty in Creating Custom family for Plumbing Fixture
    By viratmanchanda in forum MEP - Family Creation
    Replies: 2
    Last Post: September 3rd, 2014, 08:20 AM
  5. Plumbing fixture on 2 systems?
    By nick_h in forum MEP - General
    Replies: 2
    Last Post: October 16th, 2013, 03:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •